Hi all
Please help I am beyond Desperate!!! Sorry for the long post but the more info I give hopefully the more you might be able to help. I moved into a 4 bedroom house last year Oct 07 & had the above boiler installed by a reliable plumber who wasn't corgi registered but had it signed off by a corgi registered plumber. I am generally quite good with DIY but this has me stumped!
Since the installation I have had continuous problems for 12 mths with the boiler. I have gone through 4 plumbers & have been in contact with Vaillant on numerous occasions, who told me to balance the system amongst other things. I am about to go through 1 marriage as well if I cant get this resolved. Below is the issue in detail.
I have an open vented system which is fitted in a "T" plan. I have 2 zone valves, 1 for hot water & 1 for heating. I have a Grundfoss 15-60 pump & a large cylinder - all in the upstairs bedroom & the Boiler downstairs in the garage. I have 14 RAD's, 8 upstairs & 6 downstairs all with TRV's. The room stat is downstairs in the entrance hall & the programmer unit is in the room upstairs with cylinder, pump etc
- When I fire up the central heating on its own via the programmer the system fires up, then goes into "high fire" & then shuts down with an S53 code which states: -
"Appliance is within the waiting period of the operation block function due to water shortage (VL-RL spread too big)"
- The only way to get the heating to work is to run the hot water as well, IE operate both zone valves.
- However by doing this the RAD's don't get that hot as the water is being split 2 ways. Only once the hot water has been running for awhile can I switch the hot water off on the programmer and then the heating will run.
In the afternoon when I get home I have programmed only the Heating to come on at 5pm, not the hot water. When I get in after 5pm the boiler is showing S53 and the RAD's are slightly luke warm.
- To resolve this I have to turn the Heating dial on the Boiler off, run the hot water via the programmer & then turn on the heating dial on the boiler and then run the heating via the programmer.
This most times gets the heating going but still get an S53 code at times during the evening.
- The system should run fine on its own without me having to do anything. The boiler is now out of Installer warranty (who wont return any of my calls anyway) but is still under the 2 yr Vaillant warranty.
Below is the series of events which lists what has been done to the system.
- Boiler installed Oct 07 and power flushed with a Magnatron (I think that's what he called it - the flusher with the magnets). (since then system been drained approx 8 times, water is crystal clear - no blocks/debris)
- Pump has been replaced 3 times with no debris found inside on any occasion
- Vaillant engineer came out, replaced the NTC's, & told me I had possible crossed pipe work. He dropped the output to 24KW. Called plumber back who confirmed piping not crossed - still not resolved.
- Another engineer came out & replaced the heat exchanger thinking it could be blocked - still not resolved.
- My plumber gave up, called another plumber - we together uncovered that the 1st Vaillant engineer had rewired the NTC's the wrong way round when he put the new ones in. We rewired correctly. They are positioned on the straight part of the pipe and not on the bends & are secure.
- Vaillant engineer came out again, changed the output back to 28KW.
- - I also kept telling everyone there was air getting in the system as I continually had to bleed the RAD's but none of them could figure it out. Called in another CORGI registered plumber to come sort this out. This CORGI plumber spotted it immediately, it was the tap on the positive side of the pump that was weeping and introducing air into the system. He has replaced this now - problem still not resolved.
- I have purged the system according to the manual and there is definately no air in the system now.
I also asked him to change the piping downstairs in D.Room (which was laid in a concrete floor) from 15mm - 22mm to increase flow as RAD not getting warm. He also tidied up the original Plumbers work to reduce the no. of bends in the pipe work. All long runs are now in 22mm with minimal no. of bends to improve flow.
- However to add to the problem, since then when heating was off and hot water on I am having reverse flow issues as well. I found the return pipe for the central heating to the bboilerin the garage was getting hot & the upstairs RAD's were getting warm. The water was eemanatingfrom the return from the cylinder to the boiler.
- To resolve this issue the plumber installed in a one way valve on the Heating Return just before where it joins with the cylinder return going back to the bboiler However whenever the heating is on the valve makes one hell of a noise as the sound ttravelsup the pipe work throughout the house, which is driving the wife mad on top of the heating not working.
- The current CORGI plumber has also installed a Manual Gate valve as the Bypass valve in the cupboard upstairs. It is connected to the flow from the boiler BEFORE the pump to the RETURN from the cylinder to the boiler AFTER the pump.
I still cant resolve the s53 issue
Please can someone help!! Everyone else has thrown the towel in on this one!!!
I have read Martin 2527's comments posted on Mon 6th Oct 08 - Vented System - Reverse Flow - I Think - but seems a little technical for me as don't quite understand but I think my problem is some how the same.
I look forward to any advice anyone has, thanks for your time!!!
Please help I am beyond Desperate!!! Sorry for the long post but the more info I give hopefully the more you might be able to help. I moved into a 4 bedroom house last year Oct 07 & had the above boiler installed by a reliable plumber who wasn't corgi registered but had it signed off by a corgi registered plumber. I am generally quite good with DIY but this has me stumped!
Since the installation I have had continuous problems for 12 mths with the boiler. I have gone through 4 plumbers & have been in contact with Vaillant on numerous occasions, who told me to balance the system amongst other things. I am about to go through 1 marriage as well if I cant get this resolved. Below is the issue in detail.
I have an open vented system which is fitted in a "T" plan. I have 2 zone valves, 1 for hot water & 1 for heating. I have a Grundfoss 15-60 pump & a large cylinder - all in the upstairs bedroom & the Boiler downstairs in the garage. I have 14 RAD's, 8 upstairs & 6 downstairs all with TRV's. The room stat is downstairs in the entrance hall & the programmer unit is in the room upstairs with cylinder, pump etc
- When I fire up the central heating on its own via the programmer the system fires up, then goes into "high fire" & then shuts down with an S53 code which states: -
"Appliance is within the waiting period of the operation block function due to water shortage (VL-RL spread too big)"
- The only way to get the heating to work is to run the hot water as well, IE operate both zone valves.
- However by doing this the RAD's don't get that hot as the water is being split 2 ways. Only once the hot water has been running for awhile can I switch the hot water off on the programmer and then the heating will run.
In the afternoon when I get home I have programmed only the Heating to come on at 5pm, not the hot water. When I get in after 5pm the boiler is showing S53 and the RAD's are slightly luke warm.
- To resolve this I have to turn the Heating dial on the Boiler off, run the hot water via the programmer & then turn on the heating dial on the boiler and then run the heating via the programmer.
This most times gets the heating going but still get an S53 code at times during the evening.
- The system should run fine on its own without me having to do anything. The boiler is now out of Installer warranty (who wont return any of my calls anyway) but is still under the 2 yr Vaillant warranty.
Below is the series of events which lists what has been done to the system.
- Boiler installed Oct 07 and power flushed with a Magnatron (I think that's what he called it - the flusher with the magnets). (since then system been drained approx 8 times, water is crystal clear - no blocks/debris)
- Pump has been replaced 3 times with no debris found inside on any occasion
- Vaillant engineer came out, replaced the NTC's, & told me I had possible crossed pipe work. He dropped the output to 24KW. Called plumber back who confirmed piping not crossed - still not resolved.
- Another engineer came out & replaced the heat exchanger thinking it could be blocked - still not resolved.
- My plumber gave up, called another plumber - we together uncovered that the 1st Vaillant engineer had rewired the NTC's the wrong way round when he put the new ones in. We rewired correctly. They are positioned on the straight part of the pipe and not on the bends & are secure.
- Vaillant engineer came out again, changed the output back to 28KW.
- - I also kept telling everyone there was air getting in the system as I continually had to bleed the RAD's but none of them could figure it out. Called in another CORGI registered plumber to come sort this out. This CORGI plumber spotted it immediately, it was the tap on the positive side of the pump that was weeping and introducing air into the system. He has replaced this now - problem still not resolved.
- I have purged the system according to the manual and there is definately no air in the system now.
I also asked him to change the piping downstairs in D.Room (which was laid in a concrete floor) from 15mm - 22mm to increase flow as RAD not getting warm. He also tidied up the original Plumbers work to reduce the no. of bends in the pipe work. All long runs are now in 22mm with minimal no. of bends to improve flow.
- However to add to the problem, since then when heating was off and hot water on I am having reverse flow issues as well. I found the return pipe for the central heating to the bboilerin the garage was getting hot & the upstairs RAD's were getting warm. The water was eemanatingfrom the return from the cylinder to the boiler.
- To resolve this issue the plumber installed in a one way valve on the Heating Return just before where it joins with the cylinder return going back to the bboiler However whenever the heating is on the valve makes one hell of a noise as the sound ttravelsup the pipe work throughout the house, which is driving the wife mad on top of the heating not working.
- The current CORGI plumber has also installed a Manual Gate valve as the Bypass valve in the cupboard upstairs. It is connected to the flow from the boiler BEFORE the pump to the RETURN from the cylinder to the boiler AFTER the pump.
I still cant resolve the s53 issue
Please can someone help!! Everyone else has thrown the towel in on this one!!!
I have read Martin 2527's comments posted on Mon 6th Oct 08 - Vented System - Reverse Flow - I Think - but seems a little technical for me as don't quite understand but I think my problem is some how the same.
I look forward to any advice anyone has, thanks for your time!!!