hi can you email the comment on the rt500.i am having the same problem
have 2 pipe stats connected one in attic and garage..thanks terry


"]
The reason the stat is coming on during the night/ always being on is setting number 5, there are 5 settings on the Salus

1 is the time you want heating on eg, 07.00 and set the temp (20)

2 is the time you want it to go off eg, 10.00 and set the temp (10 this will turn it off)

3 is the time to come on an evening eg. 17.00 and set the temp (20)

4 is the time you want it to go off eg, 23.00 and set the temp (10 this will turn it off)

5 the problem many people have is that they do not set number 5 correctly, this is a night/ frost stat and if you don't set the time and temperature same as 4 ie, 23.00 and 10*c then the heating will stay on.

I have had quite a few customers who struggle with the instructions so i typed it out in plain English as a word document and give it to them so its easier, if you want send me your e-mail address and i will mail it to you.
[/quote]
 
Sponsored Links
You're quoting from a 4 year post (almost). Don't think you'll get a response.
 