SANISPLIT 3 backflow problem

Joined
29 Jun 2011
Messages
12
Reaction score
0
Location
London
Country
United Kingdom
Hi, This is my first time on this forum so please forgive any mistakes. I have just installed a sanisplit 3 which will be used to pump kitchen waste around 5 metres vertically into my loft then over to my downpipe. I have tested it using clean water from the sink and the problem is once the water is pumped up the vertical pipe the pump starts up every 2 minutes or so because the water has run back. If I switch the sanisplit off water flows back into the sink. The pipework is 40mm as recommended by the sanisplit technical advisor. I have found 40mm non retrurn valves and think this might work, but has anyone got any advice or tips for me?
Thanks.
 
Sponsored Links
42mm flap valve (NRV) should be installed to vertical run close to unit.
 