The 100A sticker doesn't mean there is a 100A fuse in it.
Well, one has to believe some things - and "100A Fuse Fitted" seems about as clear as it could possibly be!The 100A sticker doesn't mean there is a 100A fuse in it.
That's not what is says! The carrier/housing will probably have the 100A maximum rating moulded onto it somewhere - but the "100A Fuse Fitted" sticker surely could not be any more clear/explicit if it wanted to be?No, that just means the carrier is rated at 100A.
Quite so - as I said a "100A Fuse Fitted" sticker is so explicit that anyone who puts it on (or allows it to stay on) when they've just fitted a fuse other than 100A really should not be doing that job!Yea, I found one of WPDs sticker sets left over in a new cutout recently. It had a nice selection of L1,L2,L3&N markers, 415/230v stickers and it had a selection of fuse carrier labels, 60/80/100A, also had the BS number for the fuses, so I would suspect there's no excuse to put the wrong sticker on. Probably something they could get disciplined for
... but I don't think we are, after diversity. As I said to the OP, there probably aren't that many installations for which adding up all the potential 'maximum loads' would not produce a figure in excess of the rating of the cutout fuse. Don't forget that the DNO would probably regard the average load of the OP's installation (apply the sort of diversity that they do) as about 10A !!But don't tell Ban that we're advising putting a 100A+ load onto a 100A fuse......
Kind Regards, John
I realise that - but, to be fair to BAS, we're talking about different things. I agree with him that it would be wrong (and non-compliant) to have circuit with a design current of 26A protected by a 20A device. It would also be wrong to have an installation with a "design current" of >100A protected by a 100A fuse. However, in determining the "design current" of an installation, all sorts of diversity can be applied (hence, IIRC, DNOs regard the average house as representing a 'design load' of ~2.5kW, aka a "design current" of ~10A).It was just a dig at Ban after saying you couldn't put a 26A load on a 20A breaker.
Pathetic.we're not, I agree with you 100% there.But don't tell Ban that we're advising putting a 100A+ load onto a 100A fuse......
It was just a dig at Ban after saying you couldn't put a 26A load on a 20A breaker.
I think it really comes down to what the designer feels is the "design current". In the absence of any information about how the circuit will be used/loaded, the convention is to consider the design current of a sockets circuit to be the In of its OPD - even tghough, as you say, it's far from impossible that a greater load than that will be 'plugged in'. However, IF the designer knows, or has reason to consider 'likely', that the loading on the circuit will sometimes be some figure greater than, say, 20A, then I would say that that 'figure' becomes the "design current", so that a 20A OPD (and perhaps not 2.5mm² cable) would not be appropriate.I don't agree about the 20A breaker scenario. A 20A radial on 2.5 is a standard circuit. Of course it could be subject to 20+A of loading, just as a 32A ring final could have 32+A plugged into it.