Self-Build - Boundary Box help...

Discussion in 'Electrics UK' started by christianbeccy, 17 Oct 2021.

  1. christianbeccy

    christianbeccy

    Joined:
    23 May 2018
    Messages:
    71
    Thanks Received:
    0
    Country:
    United Kingdom
    We're in the early stages of a self-build. We plan a 3ph connection, which will have to be to a Boundary Box at 35m from the base of the pole. This is still some way from the house, probably around 50m. Is this a concern?

    There is a closer pole that is probably shortens the distance between the Boundary Box and the house to about 20m, but it's £2000 more to connect here.

    Any help is appreciated.
     
  2. Sponsored Links
  3. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,936
    Thanks Received:
    1,991
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Further away = much larger cable required and longer trench, both of which will cost more.
    Nearer = smaller cheaper cable and shorter trench, but the connection cost is more.

    All depends on the relative costs of the two options.
     
    • Thanks Thanks x 1
  4. christianbeccy

    christianbeccy

    Joined:
    23 May 2018
    Messages:
    71
    Thanks Received:
    0
    Country:
    United Kingdom
    OK great, but with cost aside is the longer run detrimental in any other way?
     
  5. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,643
    Thanks Received:
    1,746
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    The DNO are permitted to supply at a voltage of between 207 and 253 volts, and your permitted 5% on power and 3% on lighting, so it is the lighting which is real limit. My calculator only goes to 16 mm² so at 100 amp so will not work it out but would guess looking at least at 25 mm² so for 5 core looking at £20 per meter so 35 m = £700 and 50 m = £1000 however may need to go to 35 mm² which means £25 per meter so £1250 so likely cheaper for you to run cable not DNO.

    But although the likes of CEF may publish price of cable, in real terms it is negotiable, so not so easy to calculate. And not included price to dig trench.
     
  6. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,665
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Not that I can think of - if properly designed, the longer the run, the larger the cable will one use so as to get the voltage drop (and 'wasted energy' cost) down to the same level, so it shouldn't make any difference, other than in terms of cost (of both cable and its installation).

    Kind Regards, John
     
    • Thanks Thanks x 1
  7. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,200
    Thanks Received:
    556
    Location:
    London
    Country:
    United Kingdom
    You will not pay for the wasted energy though as the meter is at your end of the cable.
     
  8. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,665
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    That's true - but, as far as 'the planet' is concerned, it is still a cost in terms of wasted energy (unless you can think of some benefit which derives from 'heating the soil').

    In any event, consumers in general will ultimately pay (in £s) for un-metered energy wasted in the distribution network, since the price they pay for metered electricity will take into account the energy for which DNOs and suppliers pay which is 'expended' upstream of consumers' meters.
     
  9. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    8,483
    Thanks Received:
    1,163
    Country:
    United Kingdom
    I once saw a figure of 10 to 30% for the the overall network - Have you seen a different figure?
     
  10. Sponsored Links
  11. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,617
    Thanks Received:
    430
    Location:
    Kent
    Country:
    United Kingdom
    One only has to look at the efficiency of the network transformers of 1% to 2% and the older versions may be nearer 5% to see some huge losses.
     
  12. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,617
    Thanks Received:
    430
    Location:
    Kent
    Country:
    United Kingdom
    I doo of course mean 99% to 98% and 95%.
     
  13. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    8,483
    Thanks Received:
    1,163
    Country:
    United Kingdom
    There is a lot more to the network, before the power gets to where it is used, than just the transformer and losses are additive.
     
  14. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,665
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I don't recall having ever seen 'a figure'.

    However, it's obvious that those who do the generating the electricity will expect to be paid for all the electricity that they generate and fee to the grid, regardless of whether that energy is put to useful use by an end-consumer or is dissipated ('wasted') somewhere between the generator and the end-consumer - and that cost "of everything generated" will be passed on by suppliers to the consumers.

    My blind guess would be that an 'appreciable proportion' of the energy would not get to consumers, so I would not argue with the ballpark you mention - although I would probably have guessed nearer to 10% than 30%.

    Kind Regards, John
     
  15. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    8,483
    Thanks Received:
    1,163
    Country:
    United Kingdom
    It will of course vary with the load - transformers, up to a point, become more efficient as their load increases, where as cable efficiency is at maximum the lighter the load.
     
    • Like Like x 1
  16. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,617
    Thanks Received:
    430
    Location:
    Kent
    Country:
    United Kingdom
    Oh yes absolutely, again one only has to look at the wire strung up on pylons and although running at a tiny % of the current in an equivalent LV network the copper losses are very much still there.


    Iassisted with installing KWh in the LV side of a customers HV network and within a few weeks they started questioning the difference of a 3-4% between the 'new meters' and the 'Suppliers meters', the Transformers were ancient.
     
  17. christianbeccy

    christianbeccy

    Joined:
    23 May 2018
    Messages:
    71
    Thanks Received:
    0
    Country:
    United Kingdom
    That's the answer I was hoping for. Thanks!
     