I want to put a ring of sockets in the shed, with a separate feed for lights and some radials for sockets in the ceiling (at height).
I do have a few largish tools (thicknesser or table saw etc nothing too massive though) and the vac/dust extraction. I think that would be the most I would use at once, with some thought for a 1-2kw heater (could run a heater right by the CU with it own feed?). Not sure here if I should go for 2.5 or 4mm?
I also want to put some double sockets in the ceiling run as radials (connected from a socket in the wall, diagram doesn't show that). I doubt I would want more than 13A at a time from each double. Would 1.5mm be okay in this instance? And as described? I think the ceiling might be 101, but insulation is just PIR and ~60mm/
I expect I will be putting the wire between the insulation and inner cladding (102?) though may end up in surface conduit (B).
Lights max 10w each, x4. I'm assuming 1mm is okay here.
From what I can tell, I can do this myself, though the house to shed CU feed would need someone else to do? (Which is the plan). Would having an external socket on the shed (fed from the socket ring using an FCU) needs to be signed off being external?
Sketch: https://i.imgur.com/0bjjtBz.jpg
I do have a few largish tools (thicknesser or table saw etc nothing too massive though) and the vac/dust extraction. I think that would be the most I would use at once, with some thought for a 1-2kw heater (could run a heater right by the CU with it own feed?). Not sure here if I should go for 2.5 or 4mm?
I also want to put some double sockets in the ceiling run as radials (connected from a socket in the wall, diagram doesn't show that). I doubt I would want more than 13A at a time from each double. Would 1.5mm be okay in this instance? And as described? I think the ceiling might be 101, but insulation is just PIR and ~60mm/
I expect I will be putting the wire between the insulation and inner cladding (102?) though may end up in surface conduit (B).
Lights max 10w each, x4. I'm assuming 1mm is okay here.
From what I can tell, I can do this myself, though the house to shed CU feed would need someone else to do? (Which is the plan). Would having an external socket on the shed (fed from the socket ring using an FCU) needs to be signed off being external?
Sketch: https://i.imgur.com/0bjjtBz.jpg