No it may not.The whole point about my post is that a ring final spur may be made using 2.5mm cable and it may be derated to around 14A by the conditions its in and it may have a double 13A socket on the end of it
And the reason you see damage is because it's not in compliance with the wiring regulations.and there may be a 3Kw device pluged into each socket. And yes I have seen exactly this too many times and earnt a lot of money correcting the resulting damage.
It may be commonly encountered, but it is NOT in the regulations.NO
Thats all in the regs and may be fitted in every other house in the country.
Appx 15 states that you can fit a 2.5 unfused spur to a 32A Ring Final circuit, feeding one outlet. Or an FCU can be used to supply several outlets wired in min. of 1.5mm² T&E.
On a 20A Radial Final circuit, a minimum of 2.5mm² T&E must be used.
On a 32A Radial Final circuit, a minimum of 4.0mm² T&E must be used.
HOWEVER, an unfused spur can be taken from any point in the circuit in 2.5mm² (including at the origin of the circuit), providing it feeds only one single or twin outlet.
It seems there is a difference of opinion on the interpretation of the regs.
Simple question
Is it permissible, within the regs, to install a DSO using a 2.5mm T&E spur on a ring final without any additional protective device?