I've got a 9.5 kw shower that i put in about 6 years ago that has just decided that it wants to keep blowing its fuse.

I have about 10 -15 metres of 10mm cable(not embedded into walls) from the main fuse to the shower unit and i'm using a 30A fuse.

The fuse went once about 3 yrs ago but no probs till about 6 weeks ago.
I smelled fishy burning bakelite when the shower stopped - mid hair wash - and sure enough the fuse had gone.

Replaced fuse but i have had the same problem again 2 weeks later, and now again today.

Has anybody got any suggestions??

All i can think is the shower is getting old and needs replacing but nothing seems worn inside- no rust or wear on wires- could the heater element be shorting?? How could i test for that?

But something is drawing too much current obviously.

We do have fluctuating water pressure but not to a great degree, if that could be a possible problem, but it has always been like that.

Any help would be greatly appreciated.
 
Sponsored Links
The fishy smell will be something burning, check the switch connections and connections in the shower itself.
 
yes the fuse holder cartridge was melting, that was the fishy smell but what i really would like a bit of help with is what could be the reason for the fuse repeatedly blowing??
 
petern said:
what could be the reason for the fuse repeatedly blowing??
I think you've answered your own question here:
petem said:
I've got a 9.5 kw shower ..... i'm using a 30A fuse.
9.5kw @ 230v = 41.3A.

What type of fusebox/CU do you have, and what rating is the main switch? It may be that you can simply uprate the fuse, but in many older set-ups you must not do this. In any case you must make certain that the cable is 10mm as you say.
 
Sponsored Links
I just rechecked the wire and i got it wrong. :eek: The cable to the shower is only 6mm. :(

As to the fuse box, the house is in major need of a rewire and the fuse box is a stand alone unit connected directly to the meter.(on an old meter board)

I don't think i should uprate the fuse too high, do you think a 35A may be any better?? Don't think i should go any higher.

Also just a little confused as to why, after 6 years, it should start to pull enough current to blow several fuses
 
If a rewire is pending, your only option is not use the shower until it's done!

do you think a 35A may be any better?
Without being funny, what makes you think a 35A fuse will be any better for a 41.3A appliance? In any case, your cable is too small.

Fusewire has certain characteristics meaning it can sustain an overcurrent for a varying amount of time. You were "lucky" in the first place that it lasted so long. I'd be more concerned about the under-rated cable, which could potentially overheat causing fire.

Get around to having your rewire done ASAP. In the meantime, have a bath - it's more relaxing anyway! :D
 