SIEMENS RWB9

Discussion in 'Plumbing and Central Heating' started by thekilljoy, 1 Jun 2020.

  1. thekilljoy

    thekilljoy

    Joined:
    6 Jun 2009
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    My central heating has developed a problem in that when I apply mains power to the system but with both the HW and CH switched off (lights out) the boiler fires up and activates the pump and central heating. I cannot switch off the heating.
     
  2. Sponsored Links
  3. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    11,513
    Thanks Received:
    2,365
    Location:
    Daventry
    Country:
    United Kingdom
    Zone valve microswitch stuck on
     
  4. thekilljoy

    thekilljoy

    Joined:
    6 Jun 2009
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    But why does it trigger the boiler ignition when both CH and HW demands are switched off?
     
  5. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    2,940
    Thanks Received:
    798
    Location:
    North
    Country:
    United Kingdom
    It has a permanent live and a switched live, so basically the switch is stuck in the on position, leaving it connected, whereas your programmer would normally remove the switched power from the zone valve, the output side of the valve is receiving power because the switch is stuck open.
     
    • Thanks Thanks x 1
  6. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    11,513
    Thanks Received:
    2,365
    Location:
    Daventry
    Country:
    United Kingdom
    Because that's how they work. Programmer activates zone valve motor, which opens the valve and presses a microswitch. The microswitch contact sends power to the boiler, which fires up. If it's stuck open, it'll power the boiler at all times because the microswitch is continuing to send power to the boiler even with the programmer off
     
    • Like Like x 1
  7. thekilljoy

    thekilljoy

    Joined:
    6 Jun 2009
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    Makes sense, I assumed that the controller just caused valve to move. So is it just a case of having the microswitch replaced without touching the actual mechanical valve itself.?
     
  8. Sponsored Links
  9. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    2,940
    Thanks Received:
    798
    Location:
    North
    Country:
    United Kingdom
    Usually depends on zone valve, and whether you can solder the microswitch, probably better just obtaining a valve head.
     
  10. thekilljoy

    thekilljoy

    Joined:
    6 Jun 2009
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    Having checked the valve.

    The CH valve it is open and the lever is floppy irrespective of whether or not there is power applied to the system. Does this mean it is just motor, needless to say it is in an incredibly awkward position and I hope it is not necessary to change the whole head.
     
  11. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    15,651
    Thanks Received:
    5,607
    Location:
    Lanarkshire
    Country:
    United Kingdom
    yep the motor will have seized
     
    • Like Like x 1
  12. thekilljoy

    thekilljoy

    Joined:
    6 Jun 2009
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    As I said it is in an awkward place so although the motor replacement looks straight forward I will probably get someone to do it who has done it before and has double jointed fingers.
     
  13. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    15,651
    Thanks Received:
    5,607
    Location:
    Lanarkshire
    Country:
    United Kingdom
    post a pic of where it is located
     