Smoke alarms on an CU with 30ma main sw

Joined
1 Feb 2007
Messages
263
Reaction score
0
Location
Bristol
Country
United Kingdom
I've got a situation where I am fitting some extra sockets in a tiny cottage. The CU (manufacturer - Steeple) main sw is a 30ma RCD with 3 mcb's (sockets, Cooker & lights). The customer now wants electric smoke alarms but I cant just fit another MCB cause the main sw is a 30ma RCD.

Would you suggest I change the RCD to, say a 80A switch & then replace the sockets MCB for a RCBO & fit a 6A CB for the smokes

Or any other comments ?
 
Sponsored Links
Its a TN-S. Got a (labelled) 100A main fuse. Re-wire was done about 8 yrs ago. No main bonding.
 
Sponsored Links
What you suggest sounds fine, a 100A main switch might be better.
 
ok thanks for that :D . Need to find someone that sells Steeple stuff now. Also doing a job which requires GET MCBS. I think Denmans sell those makes.
 
Isn't Steeple a re-branded GE MCB? Same as Rexel Senates own brand Sector GE?
 
Or for the price of a 4 way board with 100amp incommer......




Good on you for making sure the smokes are not on the RCD though - Some sparks would not have bothered.
 