Socket connected to lighting ring - get rid or OK to label as 5A?

Discussion in 'Electrics UK' started by Dave Robinson, 16 Apr 2019.

Thread Status:
Not open for further replies.
  1. Dave Robinson

    Dave Robinson

    Joined:
    15 Aug 2016
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    Our porch has a cable dangling out through the ceiling straight into a twin socket four inches down, and then a cable from this down the wall through UPVC conduit to a switch which supplies the outside light through the exterior wall. This comes off the the whole-house lighting ring which is fed of a 6A MCB straight into the master switch (no RCD).
    It's there because previous owner was a mentalist and is by far one of the safer bodged aspects of our house electrics (one of the worst was the confusion over a yellow wire to a 2-way switch being mistaken as earth and being connected to the backbox; as such, the other switch didn't operate and more importantly the mounting screws on the switch that did work were live. Found that out the bad way).
    I'm redecorating the porch and want to sort this out. The sockets are useful for Christmas lights, but is it appropriate to have sockets running off a lighting main if I label them according to the amperage they can supply? Or should I just get rid?
    Thanks, Dave.
     
  2. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    4,575
    Thanks Received:
    309
    Location:
    London
    Country:
    United Kingdom
    Get rid of it. It is very bad practice to put 13 a sockets on the lighting circuit though surprisingly it is aiiowed.
     
  3. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    56,813
    Thanks Received:
    2,891
    Location:
    21st Century
    Country:
    Cook Islands
    That is perfectly acceptable. On the label you could include "from lighting circuit" or whatever.
     
    • Like Like x 4
    • Thanks Thanks x 1
  4. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,268
    Thanks Received:
    1,808
    Location:
    Oxfordshire
    Country:
    United Kingdom
    As JohnD says, it is acceptable and is specifically stated as such in The wiring Regulations.
    Do ignore Winston’s post. He has personal opinions on this (and other subjects) that he keeps pushing. In his opinion it’s bad practise, well it isn’t.
    We have encouraged him to join the committee that writes the wiring regulations and have the rules changed, but he resists our suggestions, in favour of bleating on and on and on about this.
     
    • Like Like x 3
  5. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    1,674
    Thanks Received:
    109
    Location:
    Derry, Ireland
    Country:
    Ireland
    Aiiowed?????
     
    • Like Like x 1
  6. diyer56

    diyer56

    Joined:
    26 Jun 2013
    Messages:
    192
    Thanks Received:
    26
    Location:
    Mid Glamorgan
    Country:
    United Kingdom
  7. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    21,071
    Thanks Received:
    1,910
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Odd for Winston, eye to eye contact.........:mrgreen:
     
    • Like Like x 2
  8. wrightsonm

    wrightsonm

    Joined:
    10 Apr 2019
    Messages:
    47
    Thanks Received:
    0
    Country:
    United Kingdom
    Does the neutral return to the lighting circuit? I recently had exactly this, but in my case the neutral was borrowed from the socket ring!
     

    Attached Files:

  9. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    27,688
    Thanks Received:
    2,973
    Location:
    Retired to:
    Country:
    Portugal
    Do you know why?

    What is the blue in the cable connected to - or why did they not just connect all to the socket circuit?
     
  10. donrkebab

    donrkebab

    Joined:
    15 Apr 2012
    Messages:
    507
    Thanks Received:
    25
    Location:
    London
    Country:
    United Kingdom
    Its not appropriate to have non rcd protected s/o for external use. As the s/o is for external use, it is more likely to be effected by moisture and consequent nuisance tripping of your lighting circuit, which in your case means the loss of all the lighting. I would replace the s/o with an rcd s/o, this will effectively separate internal and external problems. And marking it as 5A max would be a good idea.
     
  11. wrightsonm

    wrightsonm

    Joined:
    10 Apr 2019
    Messages:
    47
    Thanks Received:
    0
    Country:
    United Kingdom
    In my situation live and earth came from a light switch further up the wall, the wires ran under the floor to a 13a socket wire powering some led lights. The neutral from the 13a socket didnt have a neutral available in the light switch so instead someone wired it to the nearest available neutral wire which in this case can be seen as a random extra blue wire in the photo.
     
  12. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    27,688
    Thanks Received:
    2,973
    Location:
    Retired to:
    Country:
    Portugal
    So, they could have connected it all to the socket?
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    40,614
    Thanks Received:
    2,507
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Well, it would IF the OP's lighting circuit were RCD-protected (which he says it isn't).
    In the OP's present situation (no RCD at all) that might not be a bad idea (and would be necessary for compliance with current regs), but ....
    .. . even if the lighting circuit were RCD-protected (which, as above, it apparently isn't) that would be wishful thinking - in that, if there were two RCDs (one for the circuit and one in the socket) it would be essentially pot luck as to whether one, the other or both tripped in the event of a fault.

    Kind Regards, John
     
  14. donrkebab

    donrkebab

    Joined:
    15 Apr 2012
    Messages:
    507
    Thanks Received:
    25
    Location:
    London
    Country:
    United Kingdom
    Jonw2, read what I said and don't fill in non existant blanks, because I don't know what you are talking about.
     
  15. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,758
    Thanks Received:
    2,856
    Location:
    London
    Country:
    United Kingdom
    ¿Que?
     