Grid tie inverters are designed to shut down if they see anything out of the ordinary going on with the supply. So I doubt they would cause any problems in a generator fed system but you may well find they shut themselves down because the generator isn't keeping the supply within tight enough paramters.
Changeover switch in mains tails, so generator would become "DNO". No connection to the grid when gen running.
I am quoting to install a transfer switch and 100kVA generator on a site we maintain. Site supply is 270ish kVA, intention is to contactor control aircon and refrigeration, ditching this when on generator. PV is capable of an output of 55 odd kVA. Could happily kill it, just couldn't decide if including a ditching contactor was really required...
The specific instance I had was a single isolated domestic customer, supplied by a 25kVA Ground Mounted transformer. The property had 4kW of PV.
We connected an 80kVA generator to maintain supplies until we could change the transformer which had failed(difficult access)
I was concerned that the actual load could drop below 4kW at times and was unsure how the combined generator/PV system would react.
We shut the PV system down for a couple of days to ensure it was stable!