7m run of 2.5mm 3 core (P,N+E) fed from 20A MCB on RCD side of house CU, supplying a couple of double metal clad sockets, with a 5A spur for a striplight (1.5mm).
First off, current is OK for 2.5A with swa buried then clipped direct inside shed - right?
Second, allowing for 5m cabling in the shed (prob generous) in 2.5, and say 2m in 1.5 T+E in trunking, volt drop is :
12x20x0.018 = 4.32V
2x5x0.0165 = 0.165V
Total = 4.485V so 1.95% of 230V so OK on volt drop as well.
Just checking that I'm right on above as I've quickly flicked through the regs whilst I had chance, but we've had a new puppy since saturday and time to yourself is something you can forget!!!