I know this has been done before and I have searched but after trawling through many threads I just want some clarification on what I intend to do.
First off, I am a qualified electrician, however I am not a domestic spark, I am industrial so do industrial install and machine tool breakdowns/modifications. I therefor have a good understanding of electrcis in general but do not do house bashing day in day out.
I have been asked to put power onto a couple of sheds for my sister-in-law. They have already obtained some SWA, I'm guessing at 4mm (it was dark) but would prefer it to be 6mm.
There is one spare way in the CCU at house, this is on the RCD side.
I intend to bring the cable up the side of the house and into the house next to the CCU, I'll make the SWA off in a metal adpatable box and pass the stripped cores straight through to the CCU. At shed end I will bring the armoured up into the shed, make it off in a metal box and take to a 32A mcb for the ring, and a 6A mcb for the lights. I will either run T+E in plastic trunking and use metalclad sockets, or will use singles in metal conduit.
First question, I would prefer to have an RCD at the shed, but as I am coming off of the RCD side at the house will this cause problems with discrimination? What type of RCD should I use?
The two sheds will be close together but not joined, they want two double sockets in one shed and one in the other, and a light in each. Am I OK using one ring main and one lighting circuit to supply both sheds? I would most likely pass the cables from one shed to the other in adaptaflex (water tight flexible conduit).
For discrimination if I use a 32A mcb at the shed I will need to use a 40A at the house - right? In which case if the cable is 4mm it will be too small. If this is the case could I use 32A at thouse CCU, and use a 25A 30ma RCD in shed ( I have one of these surplus), then 20A for ring and 6A for lights? I don't think they plan to use anything too big in the sheds, it is mainly to supply a freezer.
Finally I am unsure what to do with the earths, I forgot to check what system it is, will do when I pop over this week. I would estimate at around 40M run max. Would it be advisable to use a stake at shed?
First off, I am a qualified electrician, however I am not a domestic spark, I am industrial so do industrial install and machine tool breakdowns/modifications. I therefor have a good understanding of electrcis in general but do not do house bashing day in day out.
I have been asked to put power onto a couple of sheds for my sister-in-law. They have already obtained some SWA, I'm guessing at 4mm (it was dark) but would prefer it to be 6mm.
There is one spare way in the CCU at house, this is on the RCD side.
I intend to bring the cable up the side of the house and into the house next to the CCU, I'll make the SWA off in a metal adpatable box and pass the stripped cores straight through to the CCU. At shed end I will bring the armoured up into the shed, make it off in a metal box and take to a 32A mcb for the ring, and a 6A mcb for the lights. I will either run T+E in plastic trunking and use metalclad sockets, or will use singles in metal conduit.
First question, I would prefer to have an RCD at the shed, but as I am coming off of the RCD side at the house will this cause problems with discrimination? What type of RCD should I use?
The two sheds will be close together but not joined, they want two double sockets in one shed and one in the other, and a light in each. Am I OK using one ring main and one lighting circuit to supply both sheds? I would most likely pass the cables from one shed to the other in adaptaflex (water tight flexible conduit).
For discrimination if I use a 32A mcb at the shed I will need to use a 40A at the house - right? In which case if the cable is 4mm it will be too small. If this is the case could I use 32A at thouse CCU, and use a 25A 30ma RCD in shed ( I have one of these surplus), then 20A for ring and 6A for lights? I don't think they plan to use anything too big in the sheds, it is mainly to supply a freezer.
Finally I am unsure what to do with the earths, I forgot to check what system it is, will do when I pop over this week. I would estimate at around 40M run max. Would it be advisable to use a stake at shed?