pbar said:
FatGit said:
pbar said:
But what is to stop someone (unknowingly or otherwise) plugging in two high powered appliances and causing a potentially dangerous situation. As I understand the regs don't require an FCU for this spur either.
What's to stop somone doing this on any socket?
Because 'any socket' won't always be a spur.
On a ring, the load is spread over 2 cables.
It may well be spread over two cables, but it is only 'spread over' one sockets terminals
The answer is of course that its not a big enough problem to worry about in reality, you'd have to draw 20A+ for quite a long duration (on MK kit more than a day, on others probably less) to start causing a problem, You're unlikely to plug two heaters next to each other, You could have a rumble drier and something else, but they only run for 90mins or so, and you aren't going to have a heater next to one, you might have a washer (which I don't think runs its heater for that long, perhaps 30mins), ditto dishy washer, kettle and toaster run for about 5 mins.
So while you should avoid having them both on a double socket, it might be more worthwhile worrying about rubbishy connections in the moulded plug on the dryier, or as bernard suggests, poor fuse contact, or even weakened socket outlet bits (a much bigger problem in the US than here I understand, with plugs sometimes falling out of worn sockets, but if you've ever seen the weedy things they let pass for 15A plugs....)
Design of the BS1363 isn't amazingly great though, anyone who has had hold of a 15A BS546 will testify how British it feels