Has your RCD been tripping?No i havent but live to earth test when disconected from earth block showed me 130v

Has your RCD been tripping?No i havent but live to earth test when disconected from earth block showed me 130v

have you measured to check if there is any voltage between neutral and earth?Nothing was tripping

Sounds like reversed polarityThere was 0 between live and neutral but every socket works

OK so the picture you have posted of the earth sparking is the two earths on your ring main twisted together, have you seperated these and split the ring to see if both of them spark or just one side? I am reluctant giving much more than this on the fault finding as this is really for an electrician to checkThere was 0 between live and neutral but every socket works

My suspicion too. Possibly faulty socket outlet or damp.Sounds like reversed polarity

I fully recommend an electrician take a look asap, you are risking electrocution or losing power over xmas. That would be then difficult and expensive to remedy.I had 16v with only live conected to mcb between earth and neutral that was measured on cables not connected to terminals

On both earths or just one earth on your ring?I had 16v with only live conected to mcb between earth and neutral that was measured on cables not connected to terminals