I was called to go to the clients to check the DHWS as the plumbers and electricians are from out of town and on their weekend off or at the client's other sites.
Being the weekend I can't get hold of Stovkis and their site won't let me register
The Stovkis Econotrol control panel temperature readout on the secondary was displaying >99deg C and the high temp alarm is latched even though the pipe is stone cold, leaving the unit interlocked out.
On cleaeing the alarm and manaully getting HW into the secondary tank so they don't have to shut down their business got the Hx running again, a process I had to repeat all day.
On booting up the valve and pumps run in sequence correctly and the temperature readout is accurate. This is short lived and the temp reading displays >99deg c again, the unit goes into fualt state and is interlocked out by the BMS.
Anyone had similar problem with these Hx controllers?
I think it's a problem with the PCB than the sensor since it does at times display the correct temerature.
Ayone know what type of temp sensor it is, thermistor? t/c? Pt100? so I can try out a third party sensor just to confirm iit's not the sensor until I get hold of Stovkis. It's not in a dywell so couldn't remove it.
Being the weekend I can't get hold of Stovkis and their site won't let me register
The Stovkis Econotrol control panel temperature readout on the secondary was displaying >99deg C and the high temp alarm is latched even though the pipe is stone cold, leaving the unit interlocked out.
On cleaeing the alarm and manaully getting HW into the secondary tank so they don't have to shut down their business got the Hx running again, a process I had to repeat all day.
On booting up the valve and pumps run in sequence correctly and the temperature readout is accurate. This is short lived and the temp reading displays >99deg c again, the unit goes into fualt state and is interlocked out by the BMS.
Anyone had similar problem with these Hx controllers?
I think it's a problem with the PCB than the sensor since it does at times display the correct temerature.
Ayone know what type of temp sensor it is, thermistor? t/c? Pt100? so I can try out a third party sensor just to confirm iit's not the sensor until I get hold of Stovkis. It's not in a dywell so couldn't remove it.