Just got home to find a large vertical sunbed in my back room, turns out the wife's hired it before our holiday.
It's got 22 x 200 watt tubes in it and is fed via two leads with 13 amp plugs, one plug feeds 10 lamps and the other feeds the remaining 12.
Am I right in thinking that'd it best if I plug one lead into one double socket in the room and the other lead into another double socket in the room to try and ballance the load accross the ring seeing as I have a load of almost 20 amps at just one socket?
Cheers.
It's got 22 x 200 watt tubes in it and is fed via two leads with 13 amp plugs, one plug feeds 10 lamps and the other feeds the remaining 12.
Am I right in thinking that'd it best if I plug one lead into one double socket in the room and the other lead into another double socket in the room to try and ballance the load accross the ring seeing as I have a load of almost 20 amps at just one socket?
Cheers.