OK. This is a simplified version
So with bonding we have a touch voltage below 50V.
This is because we are not using the external R2 in out calculations.
Why the external R2 is left out confuses me, but I think this is why...
So we are not talking about EFLI and low impedances here, i.e getting a low resistance path to enable the OPD to operate in the correct time.
This is about trying to prevent as much as possible different potentials.
So the voltage on the
Extraneous CP would be considered at earth potential (0V)
If a fault were to put a voltage on the
Exposed CP . You would have a large PD between the two.
Now we have not connected that Extraneous CP to make it a more conductive path to clear a fault.
We have connected it because we want to try and equalise the difference between the Exposed CP and the Extraneous CP.
So a proportion of the fault current at the Exposed CP will ( resistance depending) appear at the MET.
Which will pass that voltage on to the Extraneous CP.
This will mean that the the Exposed and the Extraneous CP, although at a different potential,
that potential difference is not so large, and shock risk is reduced.
What I still need to clear in my mind is what is the Voltage at the fault.
This is again what I think is happening..
The voltage 'left' after passing through R1e and R1 ( I work out at 121.12v) appears on the Exposed CP
The voltage on R2 appears ( again resistance depending ) on the MET but it has it has dropped another 32.22v
putting 88.88v onto the MET, and Extraneous CP.
This rises the voltage on the Extraneous CP to 88v.
The potential difference is the 121.12v minus the 88.88v which works out at 32.222v
(Hurray) Possibly... But I have another question
which Im not quite sure how to word yet...