Does not matter if powered on or off. A surge current is electrically different (superposition) from AC power current. A surge current may even cross a millimeters gap inside a power switch. Or simply use the other AC wire to connect to earth, destructively, via an appliance.... does the damage occur when the power cuts off or when it reinstates, or can it be from either.
A surge is a connection from the cloud to earth. That current must exist simultaneously out of a cloud as it is also flowing into earth. Your electronics must be in that path (have both an incoming and an outgoing path) for damage to occur. Obviously, AC power on or off makes little difference.
Obviously, other destructive transients (electric utility switching, squirrel shorting a transformer, etc) also create the same typically destructive transients - incoming on AC mains and outgoing to earth.Do you think surges are only caused by lightning and must be in a series path with a lightning strike ?
Problems with dis-connected or bouncing neutrals are probably far less common in the US as the distribution network is different from the UK.Maybe they don't have pikeys stealing neutral links from substations in the US of America
The term "power surge" covers a lot of different events.does the damage occur when the power cuts off or when it reinstates, or can it be from either.
A term 'surge' or 'power surge' is quite specific. From the IEEE, an overstress condition that has a duration of less than a few milliseconds. A swell is an overvoltage that can last a few cycles. You have described an overvoltage. All specifically defined by the IEEE.The term "power surge" covers a lot of different events.
He is not asking about an overvoltage. He even used the word "transient" - which says nothing about overvoltages created by copper theives or similar disturbances.... damaged from a transient peak power surge
Destructive surges typically occur maybe once every seven years. But when an anomaly causes damage, then advertising has so many automatically blaming a surge. Too many even describe a blackout as a surge.Not accurate but it seems to be a term the general public accept when something noticibly "bad" happens to thier electrical supply.
Several house fires in the US have been put down to surge protected power adapters getting very hot when subjected this this kind of extended overvoltage and setting light to their plastic casings.
I had overlooked that problem.If the neutral is lost then two 120V loads end up in series.... now the voltage across each loads depends inversely on the load impedance hence the 240V may be split, say, 180V & 60V ..... you can guess what happens!
I understood your concern. That failure would result in low or no voltage. Meanwhile, the other neutral failure is, well, that was also explained:My thoughts were directed to the loss of a neutral that affected a whole street where a high load on one phase would pull the neutral towards that phase and thus increase the phase to neutral voltage in the houses on the other phases.
Of course that is completely irrelevant to the OP's question.Better systems also earth that neutral at each subscriber connection to further make damage from some overvoltage anomalies less likely.