Hoping to run this by members to be sure all is OK.
I've got an up to 5kW load in an outbuilding.
I'm in the process of digging in 25m of 2 core SWA of the 6mm variety to a depth of 450mm, tape will be laid over at half-burial depth. Planning on using the armour as CPC, exporting the earth to the outbuilding as well (TN system).
When the cable reaches the house it'll be clipped to the wall 300mm up from ground level for a 5m run, and side-enter an outside IP66 box with appropriate glanding.
Now, what I was thinking, rather than run a short bit of T&E from the CU on the inside to the IP66 box, would it be acceptable to just run the inner part of the SWA through the wall to the CU directly, and bond a separate earth between the CU through the wall to the gland on the SWA?
I could do this both ends and therefore be doubly extra sure that any water ingress in the outside box wouldn't come into contact with live terminal blocks.
Are they any issues with doing this?
Thanks in advance.
I've got an up to 5kW load in an outbuilding.
I'm in the process of digging in 25m of 2 core SWA of the 6mm variety to a depth of 450mm, tape will be laid over at half-burial depth. Planning on using the armour as CPC, exporting the earth to the outbuilding as well (TN system).
When the cable reaches the house it'll be clipped to the wall 300mm up from ground level for a 5m run, and side-enter an outside IP66 box with appropriate glanding.
Now, what I was thinking, rather than run a short bit of T&E from the CU on the inside to the IP66 box, would it be acceptable to just run the inner part of the SWA through the wall to the CU directly, and bond a separate earth between the CU through the wall to the gland on the SWA?
I could do this both ends and therefore be doubly extra sure that any water ingress in the outside box wouldn't come into contact with live terminal blocks.
Are they any issues with doing this?
Thanks in advance.