Switch ‘RCD Controlled Circuits’ tripping after new extension

Discussion in 'Electrics UK' started by steveinoz01, 10 Dec 2017.

  1. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Something is wrong, but the behaviour you describe is normal - MCBs always remain on when an RCD trips.
     
  2. Sponsored Links
  3. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,167
    Thanks Received:
    854
    Country:
    United Kingdom
    To the OP, was it the big switch ban all sheds has circled that tripped? And not the similar one further to the left that says main switch? If you switch off the"oven" switches does the ovens "cookers" go off? How about the switches marked "hob"
     
  4. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom


    Steve - do the ovens go off if you turn off the other RCD?
     
    • Like Like x 1
  5. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,167
    Thanks Received:
    854
    Country:
    United Kingdom
    Ban all sheds I just want to confirm everything as there appears to be some switch confusion, and the op admitted it was very busy in the house at the time.
     
  6. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    2,497
    Thanks Received:
    459
    Location:
    Durham
    Country:
    United Kingdom
    You appear to have 2 RCDs in that board- one (in the middle) is labelled as MAIN SWITCH which isn't helping anyone
     
    • Like Like x 1
  7. Sponsored Links
  8. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    42,464
    Thanks Received:
    2,697
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    That was first noted right at the start (post #4). However, that second RCD (the one presumably serving the two circuits labelled 'ovens') is apparently not tripping (when, I think we are being told, the ovens stop working).

    Kind Regards, John
     
  9. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    2,497
    Thanks Received:
    459
    Location:
    Durham
    Country:
    United Kingdom
    Oops- missed that. soz :(
     
    • Like Like x 1
  10. steveinoz01

    steveinoz01

    Joined:
    26 Jul 2014
    Messages:
    90
    Thanks Received:
    3
    Location:
    Warwickshire
    Country:
    United Kingdom
    Just to close off my original post - the electrician finally came back and disconnected each competent one at a time. It took a few visits as the tripping out would sometimes take a few days to reoccur. Eventually he checked the smoke alarms and found a wrong connection and we have not had the switch trip for about a week. Fingers crossed this was the only problem causing it to trip.
     
    • Like Like x 2
  11. Iggifer

    Iggifer

    Joined:
    8 Sep 2011
    Messages:
    4,637
    Thanks Received:
    586
    Location:
    Warwickshire
    Country:
    United Kingdom
    Good news but that’s odd. Smokes are powered 24/7 so should have caused the problem consistently but if it’s fixed it’s fixed
     
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page