if you don't get heating, test the white wire, then the orange wire with HTG only on. if orange fails.... motor/actuator is faulty!
OK so far!Turn the power off to the system completely (just setting the timer to CH OFF and HW OFF is not sufficient) so the mid position valve resets to the HW port open position.
Set HW and CH timers to OFF ( DONE)
Turn HW and CH stats to minimum (DONE)
Turn electricity on (DONE)
Turn HW ON at timer and HW stat to MAX - the boiler should light. (YES)
The white gets its power from the CH room thermostat. Could this be faulty? You need to disconnect the white wire and measure the voltage on the loose white wire. If it is zero, then the wall stat is faulty. If 230v, then the white is being fed through the valve - which shouldn't happen - faulty valve.Check voltages on valve white and grey wires - should both be zero. (NO....GREY ZERO BUT WHITE LIVE, VALVE IN W POSITION)
Why NO? The voltages are correct, but the valve is not moving. This suggest a faulty motor or jammed valve.Turn CH on at timer and set CH stat to max - boiler should continue to run and rads get hot. (NO....VALVE STILL IN W POSITION - NO FLOW TO RADS)
Check voltage on White (should be 240v) and Grey (should be 0v). (NO....WHITE LIVE, GREY ZERO)
So why is the white showing zero volts? It should be 230 as it is fed from the CH roomstat. Another indication that the stat may be faulty. Check the voltages at the stat terminals.Turn HW stat to MIN - boiler should continue to run. (NO...STOPPED)
Check voltage on White (240v) and Grey (240v) (NO... WHITE ZERO, GREY LIVE)
Voltages OK but boiler not working. This says that the orange wire is dead. Disconnect the orange and check voltage on loose end. If zero, the valve is faulty.Turn HW OFF at timer - boiler should continue to run. (NO....STOPPED)
Check voltage on White (240v) and Grey (240v). (YES BOTH LIVE).
Have you checked that the correct links are in place on the LWC1?In each case I am measuring the voltage between the BLUE (Neutral) and the wire in question at the LWC1 wiring centre.
if ou remove all of the wires from the wiring centre, then when you do the test you wrote, the reading won't show up!!
The I test wrote WILL check that the systems wiring is all correct Quick to do with multimeter and will lead to quick diagnosis of valve as disconnection removes the possibility of stuck microswitches causing strange readings (which I suspect is happening here)please note readings on colours above refer to where they connect not the actual colours themselves
Deagle
I fixed my fault which appeared to be the same as yours (see my previous reply) by replacing the synchronous motor.
faulty motor not powering over valve to heating heating/hw.
---------------ORANGE GREY WHITE
ALL OFF -------> NO YES NO - ok
H/W ONLY-----> YES NO YES - wrong
CH ONLY -----> NO YES YES - should be live on orange
BOTH -------> YES NO YES - yes, orange will only be live cause it
in the same terminal as the hw stat live