I'm getting a builder in ti take out an external wall between by kitchen and conservatory. The builder has suggested an engineer to do the load calculations to be sure building regs are met.
What I need advice on is whether the engineer is giving us the best solution or the easiest for him to draw up.
I like to limit size of Piers protruding into the room to support the new lintel so the engineer has given 2 options:
- Steel box frame - expensive
- Piers built of engineered bricks
Engineered bricks seemed like the best for cost reasons and I asked him to see how small he could make the Pier. What he's drawn though are Piers projecting 440mm into the room, which is double what I was hoping for.
Questions:
1) The drawing shows the Pier made up of 1 skin of my current external bricks and 1 skin of 70N/mm² engineered bricks. Would it not be possible to buid the Pier of 2 lines of engineered bricks to make it stronger smaller?
The engineer's response here is only that it wouldn't make much difference.
2) The calculations show the Pier is currently spec'd to support 74kN and the factored load on it is 54kN. Would that not allow for the Pier to be ~30% smaller and still support the load?
The engineer's response here is that he has to think about latteral loads and eccentricity.
3) In the most recent communication the engineer has stated that building Regs Part A actually requires a 550mm Pier. I couldn't find that in the Part A doc, anyone heard of that?
Obviously I understand that concern 1 is that my house stands up, but for me concern 2 is that this Pier will be staring at me for the next 20 years and I just want to know that we have done what we can to minimise the projection.
Thanks,
Eddie
What I need advice on is whether the engineer is giving us the best solution or the easiest for him to draw up.
I like to limit size of Piers protruding into the room to support the new lintel so the engineer has given 2 options:
- Steel box frame - expensive
- Piers built of engineered bricks
Engineered bricks seemed like the best for cost reasons and I asked him to see how small he could make the Pier. What he's drawn though are Piers projecting 440mm into the room, which is double what I was hoping for.
Questions:
1) The drawing shows the Pier made up of 1 skin of my current external bricks and 1 skin of 70N/mm² engineered bricks. Would it not be possible to buid the Pier of 2 lines of engineered bricks to make it stronger smaller?
The engineer's response here is only that it wouldn't make much difference.
2) The calculations show the Pier is currently spec'd to support 74kN and the factored load on it is 54kN. Would that not allow for the Pier to be ~30% smaller and still support the load?
The engineer's response here is that he has to think about latteral loads and eccentricity.
3) In the most recent communication the engineer has stated that building Regs Part A actually requires a 550mm Pier. I couldn't find that in the Part A doc, anyone heard of that?
Obviously I understand that concern 1 is that my house stands up, but for me concern 2 is that this Pier will be staring at me for the next 20 years and I just want to know that we have done what we can to minimise the projection.