Small problem that I need clarification on as I can't remember 100% the correct order of events...!
To get to the point, my cylinder thermostat is not switching ON when required ... The programmer lights up for HW on but nothing. Heating is OK.
So using my multimeter, set to AC Volts, I tested and the cyilnder thermostat COMMON terminal had 236 volts, but the cylinder thermostat CALL terminal had 0.
Just to make sure the cylinder thermostat wasn't calling and in fact the cylinder thermostat switch was definitely stuck in the OPEN position, and to make sure my programmer switches HW ON /OFF switches were not faulty and sending the wrong signal(s) - I removed the HW OFF wire from the programmer, from the terminal block (the terminal block also had 2 other wires - GREY wire from 3 port valve and the Satisfied terminal from the cylinder thermostat. After removing this wire, the terminal block, which now had just 2 wires in it still had the same, 236 volts reading.
So, I now need a new cylinder thermostat. But I cannot get one until tomorrow morning. I am at work now but found this website thanks to google!!
What I can not remember is ... the correct way of getting hot water with a faulty cylinder thermostat (temporarily tonight until I get a new cylinder thermostat tomorrow). Is this way correct; if it is not or I have missed something out, i'd be absolutely appreciative if anyone can remember the way to do this trick properly...
Leave the HOT WATER OFF wire from the programmer out of the terminal block (and temp. make safe)
Then turn on just the heating at the programmer with room stat high (door open possibly to keep room temperature down).
This should then stall the 3 port valve to mid position and give heated water to both the hot water and heating circuits whist the room stat is calling, thus heating my hot water cylinder?
Is this correct, or do I need to remove another or a different wire from the terminal box?
To get to the point, my cylinder thermostat is not switching ON when required ... The programmer lights up for HW on but nothing. Heating is OK.
So using my multimeter, set to AC Volts, I tested and the cyilnder thermostat COMMON terminal had 236 volts, but the cylinder thermostat CALL terminal had 0.
Just to make sure the cylinder thermostat wasn't calling and in fact the cylinder thermostat switch was definitely stuck in the OPEN position, and to make sure my programmer switches HW ON /OFF switches were not faulty and sending the wrong signal(s) - I removed the HW OFF wire from the programmer, from the terminal block (the terminal block also had 2 other wires - GREY wire from 3 port valve and the Satisfied terminal from the cylinder thermostat. After removing this wire, the terminal block, which now had just 2 wires in it still had the same, 236 volts reading.
So, I now need a new cylinder thermostat. But I cannot get one until tomorrow morning. I am at work now but found this website thanks to google!!
What I can not remember is ... the correct way of getting hot water with a faulty cylinder thermostat (temporarily tonight until I get a new cylinder thermostat tomorrow). Is this way correct; if it is not or I have missed something out, i'd be absolutely appreciative if anyone can remember the way to do this trick properly...
Leave the HOT WATER OFF wire from the programmer out of the terminal block (and temp. make safe)
Then turn on just the heating at the programmer with room stat high (door open possibly to keep room temperature down).
This should then stall the 3 port valve to mid position and give heated water to both the hot water and heating circuits whist the room stat is calling, thus heating my hot water cylinder?
Is this correct, or do I need to remove another or a different wire from the terminal box?