Testing smoke detectors connected to Texecom alarm

Discussion in 'Alarms, CCTV & Telephones' started by Jupiter01, 20 Jun 2019.

  1. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    3,030
    Thanks Received:
    41
    Country:
    United Kingdom
    I have mains powered Aico smoke detectors connected into my alarm system.
    There is also a test/locate switch fitted in the wall which I assumed I could use for testing purposes.

    However, when I use this, it triggers my alarm (understandable...) and the dialler starts calling my nominated contacts.

    How can I use the test switch without the alarm being invoked please? Also, is a monthly check adequate?
     
  2. Sponsored Links
  3. secureiam

    secureiam

    Joined:
    20 Jun 2014
    Messages:
    5,422
    Thanks Received:
    674
    Location:
    Lancashire
    Country:
    United Kingdom
    Engineers mode?
     
    • Thanks Thanks x 1
  4. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    3,030
    Thanks Received:
    41
    Country:
    United Kingdom
    spot on. Engineers mode prevented the calls.
    Thanks @secureiam
     