Testing Supplementary Bonding

Joined
4 Feb 2008
Messages
49
Reaction score
1
Location
Lancashire
Country
United Kingdom
How do you actually test supplementary bonding. Do you just connect your LRO from pipe to pipe and if its a low reading they must be bonded. Do you not have to test back to the MET to prove the pipe bonding is connected to some electrical apparatus in the zone?
Or is it just a visual check?
 
Sponsored Links
yes just test between extraneous conductive parts and also the cpcs from each circuit in the bathroom and ecp's....read the figure should be less than 0.05 ohms
 