Yawn, I'm still doing I&T on a property....
There is another DB upstairs.
Now, I understand the principle of testing Zdb with the cpc disconnected, as with it connected it could well present a lower reading due to parallel paths etc...
In fact, I proved it. The Zdb disconnected is 0.4 Ohm.
Connected, it is 0.3 Ohm.
My confusion lies here: my r1+r2 readings are higher than the Zs values for corresponding circuits.
I can't quite get my head round it - is it the same effect?
There is another DB upstairs.
Now, I understand the principle of testing Zdb with the cpc disconnected, as with it connected it could well present a lower reading due to parallel paths etc...
In fact, I proved it. The Zdb disconnected is 0.4 Ohm.
Connected, it is 0.3 Ohm.
My confusion lies here: my r1+r2 readings are higher than the Zs values for corresponding circuits.
I can't quite get my head round it - is it the same effect?