Would appreciate some thoughts on this situation.
Customer has a high Ze reading 720 ohms
The supply cable is the two core lead sheath type.
The earth connection is a BS 951 clamp onto the lead, off to the met.
Now, the person who fitted this clamp managed to clamp it on to the heat shrink and not the lead, hence the poor reading. Looks like it has been like that for many a year. (The fact that a new CU had been fitted, and this not picked up is another matter)
A reading to the lead sheath gives a good reading, but poor from the clamp.
I contacted the DNO, who called and said its not their problem, as they did not fit it.
The only solution is to TT it or pay them to convert to TN-CS.
I think thats a bit harsh on the home owner.
How do we know they did not fit the clamp - I have read of plenty of posts where DNO types have said they used these clamps in the distant past.
So if they supplied it they have a duty to maintain it.
The DNO chap said I should just put another clamp on the cable !
I am not happy screwing a clamp onto an old lead cable, so thats not happening
Do the DNO still attach an earthing conductors to lead sheath?
So if the DNO keep the stance that its nothing to do with them, what about the fact that this is exposed earthed metal coming into a property, so surly this needs to be connected to the MET.
An electrician can't do that. We keep being told we can't touch their stuff- and I don't want to anyway.
If I TT it you could have two different earths ?
Appreciate thoughts
Thanks
Customer has a high Ze reading 720 ohms
The supply cable is the two core lead sheath type.
The earth connection is a BS 951 clamp onto the lead, off to the met.
Now, the person who fitted this clamp managed to clamp it on to the heat shrink and not the lead, hence the poor reading. Looks like it has been like that for many a year. (The fact that a new CU had been fitted, and this not picked up is another matter)
A reading to the lead sheath gives a good reading, but poor from the clamp.
I contacted the DNO, who called and said its not their problem, as they did not fit it.
The only solution is to TT it or pay them to convert to TN-CS.
I think thats a bit harsh on the home owner.
How do we know they did not fit the clamp - I have read of plenty of posts where DNO types have said they used these clamps in the distant past.
So if they supplied it they have a duty to maintain it.
The DNO chap said I should just put another clamp on the cable !
I am not happy screwing a clamp onto an old lead cable, so thats not happening
Do the DNO still attach an earthing conductors to lead sheath?
So if the DNO keep the stance that its nothing to do with them, what about the fact that this is exposed earthed metal coming into a property, so surly this needs to be connected to the MET.
An electrician can't do that. We keep being told we can't touch their stuff- and I don't want to anyway.
If I TT it you could have two different earths ?
Appreciate thoughts