I'm not at home to test it for a bit.How is the stat behaving now @collinsc ??.
Will report back in future.
Thanks
I'm not at home to test it for a bit.How is the stat behaving now @collinsc ??.

but not a thermostat as such.
the wall thermostat bottom says hall is at 18.5ºC and the TRV says hall at 14ºC. The wall thermostat is higher, and closer to the centre of the house, the TRV both lower, and likely in the draft from the cat flap. So the command "hey Google set hall to 16ºC" will set both to same temperature. Nothing will happen as wall thermostat showing 18.5ºC, unless either the living room,
calls for heat, or bedroom calls for heat
so it all gets rather complex.HiI'm not at home to test it for a bit.
Will report back in future.
Thanks
Thanks for all your help thus far.They are the default settings, also check Cycle ratio 2:Cr, it defaults to 6 (cph, cycles per hour)
Even though it doesn't state it, I would think that controller has TPI control, normally, these controllers will demand continuous firing when the SP/flowtemp dT is 1.5C or greater (with your setting of 1.5C), once the dT is less than 1.5C then the TPI control takes charge and cycles the boiler on/off until it reaches a practically zero dT.
So, what is happening now with that controller, have you checked that the boiler is actually running when there is a indicated demand, get the boiler to fire one way or other even if you have to increase the SP to get a > than 1.5C dT, then see what happens?
Not if you are running it at about 16 degrees just to make sure it doesn't go too low for the morning, and if it is only overnight it isn't 24hrsDepends how close the thermostat is to the nearest heat source , too far away and there will be a noticeable lag in achieving the set temp.
You must be very rich to run heating 24 hours .
Oh so you have the heating off during the day. ?Not if you are running it at about 16 degrees just to make sure it doesn't go too low for the morning, and if it is only overnight it isn't 24hrs![]()
Yes. Most of the time the heating is off during the day.Oh so you have the heating off during the day. ?
Very strange.Yes. Most of the time the heating is off during the day.
We’re not in during the day so why would we want to have the heating on…Very strange.
Sorry if I have been confusing….I think you said that if you increase the required roomtemp (in the morning) from 17.5C to 18.0C? or whatever, that the boiler fires and the room then heats up?, obviously not the way that you would like it to perform though.
Sorry if I have been confusing….
We set it overnight, say to 16 or 17, so that IN the morning it is that temperature.
I do not actually set it IN the morning.
Ok- understood… now.Understood, but if the displayed temperature is within 1.5C of the required (setpoint) temp then the boiler will not fire, so if the required temp is say 17C and the displayed (actual) room temperature is 16C then the boiler will not or shouldn't fire because of this, it should fire at 15.5C or very slightly less, the question I asked was if you increase the required temp to ensure a difference of 1.5C or slightly more does the boiler then fire, as it should.