Tiger loop position question

Discussion in 'Plumbing and Central Heating' started by Rob G, 25 Aug 2020.

  1. Rob G

    Rob G

    Joined:
    26 Nov 2007
    Messages:
    24
    Thanks Received:
    0
    Location:
    Edinburgh
    Country:
    United Kingdom
    I've had a look through the previous Tiger loop queries but can't find anything that addresses this.

    By coincidence one of the search finds was a guy doing the same as me - that is replacing an external Camray oil boiler with Grants equivalent, but his question was different.

    My problem is that Grants instruction book says that the Tiger loop must be mounted at the same level or above the burner - and Grant's technical help says the same as that is what the manufacturer, Anglo Nordic says. But go to Anglo Nordic's website and the installation instruction says "as close as is practical", and that is how mine has been for 25+ years in a box, along with the filter and fire lockout, immediately below the boiler casing. And it has always worked !!

    Can anyone comment please.

    Thanks
    Rob
     
  2. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,783
    Thanks Received:
    1,096
    Country:
    United Kingdom
    I have seen many that are well below the burner operating without any problem.

    I guess you have a wall mounted boiler.
     
  3. Sponsored Links
  4. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,425
    Thanks Received:
    3,104
    Location:
    Daventry
    Country:
    United Kingdom
    Buy a Hounsfield instead - a superior boiler at a cheaper price with a longer warranty, and no Tigerloop required
     
  5. Rob G

    Rob G

    Joined:
    26 Nov 2007
    Messages:
    24
    Thanks Received:
    0
    Location:
    Edinburgh
    Country:
    United Kingdom
    Thanks for getting back Terry

    Oops - I should have said that it is an external wall hung.

    I'm now told by the guy who will commission it for me that this is an OFTEC/BSI requirement, so I have no option, but the nett result cannot ever be as tidy and out of visual impact as the neat box I currently have - grrrr!
    Rob
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page