Can anyone help, been given the following question:

• What fault level would be present at the source, feeder 1 and at the load for a system comprising:

Source = 0.050pu.
Transformer = 0.15pu.
Transformer = 0.30pu.
Feeder 1 = 0.50pu.
Feeder 2 = 2.0pu.
Feeder 3 = 7.0pu.

Anyone got any ideas?
 
Gibby106141 said:
Anyone got any ideas?

when being taught, if you don't understand ASK!

this is a diy forum, not an information beaureau
 
Breezer, I suppose I deserved that, could anyone point me in the right direction though?

Regards

Mark
 
Try the Power sector forum on the IET website.I think you have some parameters missing from that question!
 
If the transformers were in parallel, unlikely due to the difference in the pu values of impedance, and the feeders are from a common bus after the tfrs: -
Fault Level Source = 0.050pu.
Fault Level Transformer = 0.050 + (0.15 × 0.30)/0.45 = 0.1pu.
Fault Level Feeder 1 = 0.50 + 0.1 + 0.05 = 0.65pu.

Again, I doubt whether the transformers are in series, if you had a SLD, it would be clearer. The p.u. values are calculated similar to resistances in parallel or series.

Jaymack
 
It is also based on a 10MVA base, can someone at least help me with the calculation?
 