We installed a new split load consumer unit in a large country house about 2 years ago. No Leakage protection existed before and there were a few faults that had to be sorted. A Neutral/Earth short in one socket and very rat chewed cables replaced. The system worked fine until recently. The RCD trips for no apparent reason. Another (MK) unit was substituted but the fault remains. Trouble is no particular circuit seems responsible for the tripping. All MCBs have to be turned off before the RCD will reset. Whilst turning on the circuits one by one even in different order any one with an apreciable load attached will cause RCD to trip.
This fault is very strange and has got me completely stumped. I do not have a megger tester but do have a very good quality DVM.
1. What is the correct way to test all these circuits?
2. Should Neutral be tied to Earth inside supply termination box, ie. before the main company fuse?