- Joined
- 27 Jan 2008
- Messages
- 29,808
- Reaction score
- 3,696
- Location
- Llanfair Caereinion, Nr Welshpool
- Country
I did test the RCD and the insulation resistance, it was only the leakage I failed to test.Unless one's name is eric![]()
If the RCD has tested satisfactorily and does not trip with the circuit loaded, that will at least give you an upper bound for the possible 'earth leakage', even if you haven't measured it.I did test the RCD and the insulation resistance, it was only the leakage I failed to test.
Indeed. Many people's first thought seems to be to blame the device, although that very rarely is the reason - even if it is one of those 'nuisance RCD trips' which some of us seem to suffer (and which, again, are very rarely due to a faulty RCD).
I must admit, early days I would test the RCD with the MCBs turned off, I now realise the problem with that, however not sure on the way around the problem.Older RCD's (and some brand new ones) are prone to becoming more sensitive and therefore trip well below 22mA - hence why ramp testing RCD's is the first thing to do
So big question, can thesecause a problem with RCDs? It seems they put a high frequency signal superimposed on the mains, so would expect these would need a type F RCD, and not seen any in real life.![]()
With a display showing 2 decimal places (of amps), a reading of "0.01 A" could, if perfectly accurate, obviously (just by 'rounding') be indicating a current anything between 5 mA and 14.9999 mA. Any current less than 5 mA would display as "0.00 A" and any current between 15 mA and 24.999 mA would display as "0.02 A".When I lived in that house, the clamp-on I had measured in 10 mA increments, so I suppose could have had 9 mA leakage.
I don't doubt that that sometimes happens, but I think that 'drift' of the trip threshold in the other direction ('up') is far more common, isn't it - not the least due to 'stiction', particularly if RCDs are not 'exercised' (by testing) fairly regularly!Not sure I agree with this. Older RCD's (and some brand new ones) are prone to becoming more sensitive and therefore trip well below 22mA - hence why ramp testing RCD's is the first thing to do
On the face of it, I don't find it easy to think of a likely mechanism for a shift in the direction you suggest.
In any even, I still stick with the view I expressed - that 'unexplained' ('nuisance') RCD trips are only rarely due to the RCD being 'out of spec', since when such issues are investigated by testing the RCD, it is nearly always found tobe 'within spec'. Don't forget that even a brand new "30 mA" RCD is 'allowed' to trip at a residual current of about 15 mA.
Hardly a helpful comment .... what exactly do those many years at the coal face indicate?Many years at the coal face trumps DIY opinions
Hmmmm....Many years at the coal face trumps DIY opinions
I do sometimes wonder what on earth he was doing during all his years at the coal face (whilst you, and even I, were testing many RCDs!).Many years using a pick and shovel versus 60+ years of precision electronic/electrical experience...![]()
Certainly not thousands for me, but probably at least a hundred or two, and my experience has been the same as yours - and, as I implied, of the few I have found to be 'out-of-spec, nearly all have had too high a trip threshold.However I've dealt dealt with hundreds, if not thousands, of RCDs and RCBOs and I think it's fair to say the number which have any issues I can count on my hands and that includes the versions with disconnected functional earths.
Maybe, but if they were last 'switched on' 10 years ago (and, yes, even I have seen some of them), there will have been a faiir amount of opportunity for 'stiction' to set inI wouldn't really expect much stiction, because both RCD's, RCBO's, and MCB's are well 'wound up' mechanically, by the process of switching them on.