It sounds like several items are leaking small amounts which accumulate to enough to trip the RCD.A couple of years ago the RCD started tripping when both the garden lights AND garden water feature pump were on at the same time, however each works fine on its own i.e. switch the pump on and it will be fine all day, or switch the lights on in the evening (without the pump also being switched on) and the lights will be okay. Sometimes, both can be switched on and it takes some time before the RCD is tripped, sometimes it happens instantly! As the RCD also protects other circuits in the house, including the modem/router, it's a real pain when it trips! If only RCBO's had been available when the CU was upgraded in 2014!!!
Hi Conny, I tried all of that when the issue first started occurring, but whenever ANY of the lights were connected and turned on at the same time as the pump, it would trip. I tried every possible combination of lights with pump. I guess you might assume it is therefore the pump that is the issue, but having installed a brand new pump, it hasn't resolved itself.You can begin to narrow it down by removing the swa to one set of lights and running the other 2 sets with the pump on. If it trips, replace the one that you removed and remove the next one. Repeat the test with lights and pump running. If it trips, repeat with next set and finally with the 6 LED wall lights.
If at any time the circuit doesn't trip with one section disconnected, this indicates that the disconnected set is the faulty one. You can then dismiss having to upheave anything connected to the operating lights.
Yes, that's where I'm at now. I need a good troubleshooting electrician with the right equipment to track down the cause.It sounds like several items are leaking small amounts which accumulate to enough to trip the RCD.
It needs testing with the appropriate equipment.
Yes, I agree, as well as the inconvenience of multiple circuits being switched off!One of the problem with a single RCD, is that leakage on different circuit, can accumulate to be enough to cause a trip - on their own they are not enough.
It would be much better if RCBO's were being used instead of a mix of MCB's and RCD's. At least then it would 100% identify the circuit having the problem, and would also lessen the impact when it did trip.
These are operating on 230 V AC on an MCB "protected" by a RCD - which is probably "protecting" other circuits.I'm happy to supply details here, but suspect getting to the bottom of the issue is likely to be beyond my knowledge and capability as I've already tried everything I was able to and I think it now needs a qualified electrician with the necessary tools to properly troubleshoot.
Back in 2017 as part of a garden makeover we had some garden lights and a water feature pump installed. The garden circuit is on its own MCB in the consumer unit and is protected by RCD. Two switches in the house control the garden lights and garden water feature pump so they can be operated independently of each other.
RCBOs are now available.A couple of years ago the RCD started tripping when both the garden lights AND garden water feature pump were on at the same time, however each works fine on its own i.e. switch the pump on and it will be fine all day, or switch the lights on in the evening (without the pump also being switched on) and the lights will be okay. Sometimes, both can be switched on and it takes some time before the RCD is tripped, sometimes it happens instantly! As the RCD also protects other circuits in the house, including the modem/router, it's a real pain when it trips! If only RCBO's had been available when the CU was upgraded in 2014!!!
You have gone to a lot of trouble and expense when you could have replaced the "problematic" 230 V AC system with an "Extra Low Voltage" system, supplied via one or two transformers/power-supplies.In an attempt to troubleshoot the issue, a number of garden lights have been isolated completely. For the remaining lights underground connectors have been replaced with above ground IP66 rated junction boxes and the water feature pump has just been replaced with a brand new pump.
There is a "wiring box" in the garden near to the house. Two SWA cables run from the house to this wiring box, then 4 SWA cables run around the garden; 1 to the water feature pump and 3 to various light fittings. Each run of SWA to the light fittings has no more than 2 "spike" type lights fitted each with a 5W GUI10 bulb. An additional outdoor cable runs from the wiring box to 6 LED wall lights. The water feature pump uses 16W maximum.
So, in total there are 12 LED garden lights plus the water feature pump.
My experience of using transformers is that they end up costing more than the fittings when they need to be (regularly) replaced.These are operating on 230 V AC on an MCB "protected" by a RCD - which is probably "protecting" other circuits.
It would be better if the "garden circuit" was "protected" by a RCBO.
A "fused" Extra Low Voltage power supply will have few problems concerning "leakage" - due to Garden Moisture.