TT Earth Loop Impeadance, stangley odd

Joined
4 Nov 2007
Messages
97
Reaction score
0
Country
United Kingdom
I am currently carrying out a new installation in a new kitchen extension, the whole house was tested last year, the customer gave me the results so I could compare against mine to determine any detrioration.

MMMmmmmmmm, its a TT supply, they test value of the ELI done in 2008 was 4.7 ohms, my measurement is 42.3 ohms, I have checked the earth stake and the continuity to it, all is ok, undisturbed.

100mA RCD, just kind of wonder why the huge difference, would it be advisable to bang some more stakes in to lower this reading?
 
Sponsored Links
Joined
27 Jan 2008
Messages
19,492
Reaction score
1,851
Location
Llanfair Caereinion, Nr Welshpool
Country
United Kingdom
I will guess the last guy did not test rod but tested the whole installation.

Reading you have is fine that is what you would expect.

4.7 ohms with earth rod would be very hard to get. I fitted 100's of rods around a gas terminal and we wanted 8 ohms per rod. To get that needed 4 to 8 rods and only way one can drive them in is with a paddies motorcycle.

I would not think anyone on a normal building site would ever be able to drive in 8 rods even 4 rods would be hard going so I would think he has measured it with water, gas etc still connected to get readings that low.
 
Joined
4 Nov 2007
Messages
97
Reaction score
0
Country
United Kingdom
Thnx guys, Zdb was tested and gave .47 ohms, the pscc then is 5A, its just a high reading as compared before, this was from a NICEIC contractor, so made me stand up and think, also measurements were made with no bonding in place by me..
 
Joined
2 Jun 2005
Messages
14,841
Reaction score
477
Location
Cumbria
Country
United Kingdom
50p says PSCC isn't 5A!
He may have tested Ze (Ra) when it was raining so results differ.
As long as Ze is below 200 ohms it isn't a problem.
 
Sponsored Links
Joined
2 Jun 2005
Messages
14,841
Reaction score
477
Location
Cumbria
Country
United Kingdom
PSCC in a single phase is P-N, if you have a 3 phase system it is the greatest of the P-N and the P-P readings.
 