On a TT earthed system is there an easy way to ensure the integrity of the earth if you cannot locate the earthing rod?
The system has a split load CU with a 100mA time delayed RCD protecting the whole installation and a 30mA RCD protecting all 4 ring mains so I'm relatively happy that the installation is safe.
There is what appears to be a 6mm2 earth cable from the earthing block which runs off under the upstairs floor but, as I cannot locate the earthing rod, it would be good to find out if the installation is adequately earthed.
Also, there doesn't appear to be any bonding to either the incoming water and gas pipes at the point at which they enter the property (i.e. where it should be) though I haven't checked for continuity between the CU earth and the pipework so it could be bonded anywhere I guess and without being able to disconnect this (if it is connected) I can't see how I could check the main earth.
How would the experts do it?
The system has a split load CU with a 100mA time delayed RCD protecting the whole installation and a 30mA RCD protecting all 4 ring mains so I'm relatively happy that the installation is safe.
There is what appears to be a 6mm2 earth cable from the earthing block which runs off under the upstairs floor but, as I cannot locate the earthing rod, it would be good to find out if the installation is adequately earthed.
Also, there doesn't appear to be any bonding to either the incoming water and gas pipes at the point at which they enter the property (i.e. where it should be) though I haven't checked for continuity between the CU earth and the pipework so it could be bonded anywhere I guess and without being able to disconnect this (if it is connected) I can't see how I could check the main earth.
How would the experts do it?