Guys, hope you can help.
First thing, i am a spark but need some advise. i've been looking at a job today for a farmer friend. he's just built a new plant shed which is about 5-6000 sq ft and about 30ft to the apex. the plant shed is the outskirts of the yard about 150mtrs from the incomer. The supply to the farm is 100amps TP&N TT. He wants a 45amp TP&N supply to the new barn which should be fine with a 16mm 4core. i'm going to up-grade his incoming switch gear and split off some of the sheds as follows
100amp 100mA DT RCCD feeding 3no 63amp 100mA RCCD's for other loacl submains, including the new shed
in the new shed i was going to install a 6way TPN MCB dis board to serve the lights, general power and some small plant.
is it best to make the new shed TT and put a new rod down, or use the existing earth at the intake and take it to the shed. The other problem is the new shed has an electric roller shutter so i dont want to feed this via an RCCD located in the shed because if it trips, there is no other way in.
I know as its a farm the lower value of 25v applys for RCD's calcs but i'm not sure about not having an RCD on the incomer in the shed
I hpe this make's sence
First thing, i am a spark but need some advise. i've been looking at a job today for a farmer friend. he's just built a new plant shed which is about 5-6000 sq ft and about 30ft to the apex. the plant shed is the outskirts of the yard about 150mtrs from the incomer. The supply to the farm is 100amps TP&N TT. He wants a 45amp TP&N supply to the new barn which should be fine with a 16mm 4core. i'm going to up-grade his incoming switch gear and split off some of the sheds as follows
100amp 100mA DT RCCD feeding 3no 63amp 100mA RCCD's for other loacl submains, including the new shed
in the new shed i was going to install a 6way TPN MCB dis board to serve the lights, general power and some small plant.
is it best to make the new shed TT and put a new rod down, or use the existing earth at the intake and take it to the shed. The other problem is the new shed has an electric roller shutter so i dont want to feed this via an RCCD located in the shed because if it trips, there is no other way in.
I know as its a farm the lower value of 25v applys for RCD's calcs but i'm not sure about not having an RCD on the incomer in the shed
I hpe this make's sence