TT system and RCBO's
STI
5 Aug 2009
Birmingham
Im trying to get my head around the CU requirements for a TT system. If i was to fit a CU with RCBO's protecting all the circuits, would the main CU switch 100A or 63A need to be a time delayed RCD or could it just be a straight forward isolator switch as the RCD protection is provided by the individual circuits RCBO's.
The current set up is 3036 rewirables with a voltage operated earth leakage type D isolator switch between the main fuse and the CU.
So would i need an RCD isolator between the main and the CU then a main switch in the CU which is a time delayed RCD then to individual circuit RCBO's.
Seems an awful lot of RCD type protection and i still have a single failure point in two places.
I am aware this is all notifiable but i am at my planning stage.
If all circuits are on 30mA RCBO's, no further RCD protection is needed. The main switch provides double-pole isolation. See p. 16 OSG, Fig 2.3
Futher consideration needed if you wish to be able isolate part of the installation.
  • Thanks
Reactions: STI
Indeed. In fact, as recently discussed here, not only is further RCD protection not required in that situation, but it is also undesirable ... a N-E fault tripping any of the (assumed single-pole) RCBOs would probably also take out an up-front RCD (even if time delayed), thereby taking out the whole installation and defeating the point of having separate protection for each final circuit.
Kind Regards, John
  • Thanks
Reactions: STI