Sort-of. An MCB is required to allow 113% of rated current to flow indefinitely without tripping, and must trip within 1 hour with 145% of rated current. I'm not sure of the 'indefinite time' figure for a re-wireable fuse, but the current needed to blow it within an hour is about 200%. 145/200 = 0.725, hence that 'correction factor'.Thanks, that clears it up now.So the only reason, from my understanding, is that a 20amp re-wire able fuse would hold an over current condition longer than an MCB. MCBs start their trip curve around 125%, correct?
BTW, this only applies to re-wireable semi-enclosed fuses (like our BS3036). With ('enclosed') cartridge fuses one use sue the same figures as for MCBs.
Kind Regards, John