I’m getting conflicting advice. Can anyone steer me to the correct answer please?
Situation: a small shed/garage with an electricity supply from a landlord. It’s close to the main building. A separate standing charge is paid, which is nuts.
A little while ago, during refurbishment works in the main building, we told the electricians that we would in due course want to run the shed off the main building CU.
A dedicated pair of 2.5mm T&E cables were run from the CU location to the edge of the building, about 4m from the shed, for later connection.
A 6mm SWA cable has now been run from the shed to the pair of 2.5mm T&E.
Another electrician has said one ought not to use both 2.5mm cables, only one. In case one fails and you wouldn’t know.
The loads in the shed would be low: a washing machine and lighting. Occasionally power tools. 99% of the time, zero load.
If one were to connect a 13A socket to the pair of 2.5mm cables, surely it would be a ring final? So why are we being told not to do essentially that, but with a 6mm cable going to a small CU?
I’m flummoxed!
Situation: a small shed/garage with an electricity supply from a landlord. It’s close to the main building. A separate standing charge is paid, which is nuts.
A little while ago, during refurbishment works in the main building, we told the electricians that we would in due course want to run the shed off the main building CU.
A dedicated pair of 2.5mm T&E cables were run from the CU location to the edge of the building, about 4m from the shed, for later connection.
A 6mm SWA cable has now been run from the shed to the pair of 2.5mm T&E.
Another electrician has said one ought not to use both 2.5mm cables, only one. In case one fails and you wouldn’t know.
The loads in the shed would be low: a washing machine and lighting. Occasionally power tools. 99% of the time, zero load.
If one were to connect a 13A socket to the pair of 2.5mm cables, surely it would be a ring final? So why are we being told not to do essentially that, but with a 6mm cable going to a small CU?
I’m flummoxed!