Underfloor Heating Thermostat in Bathroom?

Joined
14 Apr 2006
Messages
2
Reaction score
0
Location
Hampshire
Country
United Kingdom
Hi all,
I am planning to install electric under floor heating under tiles in our new ensuite bathroom (500w total). One problem I have is that the easiest way to feed the Thermostat/timer is via a Fused spur from a (RCD protected)ring main cable that runs under the floor along the outside wall. This therfore requires the thermostat to be sited within the bathroom on the same wall. All manufacturers, except 1 state that their thermostats must be fitted outside of bathrooms to meet wiring regulations. However, one manufacturer (Heat Mat) states that their unit has a protection rating of "IP21" and that this allows fitting within a bathroom. This is ideal for me but I am unable to verify this claim by searches on the web etc. This forms part of a greater build project which will have to be Elecrically certificated before I get the building signed off. Can anyone advise please?
Also, as the ring concerned is RCD protected at the distribution box, am I correct in fitting a starightforward spur rather the RCD spur?

Thanks
Derek
 
Sponsored Links
The normal way we connect under floor heating is to set a temperature probe into the tile adhesive along with the heat mats / wires. This is then connected to a controller, programmer and spur all located outside the bathroom. In your situation an RCD spur is not nessacery as the circuit you will be connecting to is already protected by an RCD.

Rob
 
RF Lighting said:
The normal way we connect under floor heating is to set a temperature probe into the tile adhesive along with the heat mats / wires. This is then connected to a controller, programmer and spur all located outside the bathroom. In your situation an RCD spur is not nessacery as the circuit you will be connecting to is already protected by an RCD.

Rob

Excellent - thanks. This is the route we are forced into now anyway as further research (on this forum) has identified that the IP21 rated controller could be fitted in the bathroom, but only in zone 3. My planned position unfortunately lies in zone 2 so is a no goer. Luckily I can follow your lead and feed it from the other side of an internal wall with a spur off the ring that feeds the shaver point.

Again thanks
Derek
 