advancedplumber wrote "
Unvented cylinders must be feed by the incoming water mains, which is normally well over 3 bar,"
Thats an unwise assumption to make the water authority have a statutory requirement to supply water to the main stopcock at 1 bar (equal to 15 psi). many parts of London only get say 1.5 bar however it is very subjective to where you live and the altitude. For example Frensham in Surrey has 11 bar on the main as they have to pump it out of farnham up the hills.
Tongham surrey has 7 bar.
But imagine a street where the incoming is 1.5 bar and its a street of 1 bedroom flats apartments, everyone either got a combi boiler or an unvented cylinder on electric what do you think happens to the water pressure at peak times say 7.30 am ?
Oh while we on subject "for a start most vented cylinders operate at 3.5 bar" the primary coil on a standard vented cylinder will fail at 3.5 bar.
i assume he meant unvented

The operating pressure of an unvented cylinder is set by the incoming mains pressure so if it 2.25 bar like mine is it runs at that. However when the 4 foot main burst in center of town last week my incoming gauge said 0.5 bar and it was trickling out.
Back to gowri... it unlikely you gonna be using 3 showers at once because you would empty that tank in like 5 minutes.
A stuart turner 1.5 bar shower pump will empty a 150 ltr cylinder in 6 mins flat. your only option is a larger tank and possibly and accunmulator.
http://www.gah.co.uk/heating/dualstream/introducing-dualstream.php
we quite frequently go down this route in country houses and houses that have 4-5 bathrooms.