Seems and odd question but thought i'd ask.
Local heating engineer tells me no problems, but here's my question.
System is unvented, Megalfo (10yrs old), 4yr old WorsBosch boiler. Had a problem with pressure creeping up. eventually put to bed by changing the filling loop.
When fitted system pressure was relieved and expansion valve pressure checked and found to be good t 0.5 bar as recommended. System refilled pressurized to 1 bar and air bleed off with AAV etc.
Heating and hot water works fine no problems.
Now the question.
The system pressure gauge only shows 1 bar and when system on and hot only shows 1.2bar? The system when good before always went from 1 cold to 2 bar hot?
Any ideas why the system works and only a pressure increase of 0.2bar?
No passing of water into tundish on system either.
Am I worrying about nowt or could there be another problem.