Hi i am a heating & plumbing contractor I am gas registered and have just done the unvented water course at collage .I have question relateing to a glowworm ultracom 2 35store this is a unvented cylinder and combi boiler combined .The temp relief valve comes out of the top of the boiler and has tundish suplied with it but the preassure relief vave is under the boiler conected to the preassure reduceing valve .The two items can not be conected together in the under 600mm measurement given for D1 pipe so I belive I need to fit a seperate dicharge pipe with its own tundish for the preasure relief vave discharge .Can any anyone confirm this as the book with the boiler is not clear on this .Also can I join the two D2 pipes together after both tundishs .I will be running to out side gully for discharge so i was going to run one 28mm pex pipe as it now says in G3 it is ok for pex to be used .I have seen on here that people say it ok to use polypropylene push fit waste marked pp this is not mentioned in G3 and was never talked about on the course is ok to use pp waste for the run for the two D2 pipes I know this is quite a few Questions but just trying to clear it up in my own mind as this is a fairly new model boiler glowworm have brought out .Cheers