Hi,

We had a Vaillant EcoTec Plus 832 + Rads + Filters + Plumbcentre Thermostat all installed recently.

This issue we are having is that the burner never goes into high gear, it always stays super low (on the buner scale) and rads take 1 hour to get fully hot.

I have read that these boilers are meant to go into high burn in order to get the rads / house hot quickly and then nock it down to low burn in order to maintain desired temp. But Our boiler just doesn't do this.

Any ideas?

Cheers
 
Sponsored Links
I have read that these boilers are meant to go into high burn in order to get the rads / house hot quickly


You read wrong.

What is the heatloss of your property? These boilers have an "auto" mode which is pants. They need setting to the correct loading for the property, especially if the installation isn't up to scratch.
 
You read wrong.

What is the heatloss of your property? These boilers have an "auto" mode which is pants. They need setting to the correct loading for the property, especially if the installation isn't up to scratch.

Hi,

Thanks. Yes you are correct this is it. I have just heard back from my Plumber and he also said that it needs taking off the Auto setting and that he will come around to adjust the settings to a manual KW setting based on the house / rads.

Thanks for your reply.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top