You seem to have set the flow temp to just 68 C.
In this weather you need it at about 75 C otherwise it will take ages to reach the room stat temperature as you have found.
As far as I can see your boiler is working correctly but just cycling because its seriously over rated for the house heat loss.
There ar many heat loss calc programs but most do not work well with mixed construction methods.
Tony