hi, searched and couldnt find anything similar to this fault -
Heating works fine
When demand for hot water boiler fires ok to full gas rate (10mb) then drops after about 3 secs to low rate and stays there, doesnt cut out ever, water runs at a constant 42 degs. Never gets any hotter and boiler never returns to high rate.
Flow rate is set to roughly 10 ltr/ min
WP is 21 mbars
Parts changed :
Primary thermistor
Domestic thermistor
Flushed domestic heat exchanger - re-fitted then then tried again - no diff
Replaced Domestic heat exch - no diff
Has annybody had this fault??
Also to note, before i exch thermistors i plugged a new one in dry and left existing one in for the domestic and boiler ran on full rate and water got red hot !!
I then replaced domestic therm and it returned to jut low rate??
When i ran it with primary thermisitor dry it didnt make any difference, boiler still ran on low rate for h/water.
Any Ideas would be great, cheers.
Heating works fine
When demand for hot water boiler fires ok to full gas rate (10mb) then drops after about 3 secs to low rate and stays there, doesnt cut out ever, water runs at a constant 42 degs. Never gets any hotter and boiler never returns to high rate.
Flow rate is set to roughly 10 ltr/ min
WP is 21 mbars
Parts changed :
Primary thermistor
Domestic thermistor
Flushed domestic heat exchanger - re-fitted then then tried again - no diff
Replaced Domestic heat exch - no diff
Has annybody had this fault??
Also to note, before i exch thermistors i plugged a new one in dry and left existing one in for the domestic and boiler ran on full rate and water got red hot !!
I then replaced domestic therm and it returned to jut low rate??
When i ran it with primary thermisitor dry it didnt make any difference, boiler still ran on low rate for h/water.
Any Ideas would be great, cheers.