Just starting to plan my rewire of the house and looking splitting the house in to zones. The first one I've done in consideration to voltage drop is the lounge/hall ring. my calculation is for a 38m long 'ring'.
As it's a ring do I halve the current AND the length of the circuit for the calc?
Taking into consideration you should never protect a circuit with a device rated less than the cable capacity and I'm using a 32amp rcbo, my cable 'in use' needs to be rated at 32 amps which I presume even with diversity of use etc taken into consideration I should use 32A for the voltage drop calc?
If I'm halving the curernt AND length I get
2.5mm cable 18mv/m = 18x19x16/1000 = 5.4 volt drop
If I halve just the current (which makes no sense in my head??) I get
2.5mm cable 18mv/m - 18x38x16/1000 = 10.9 volt sdrop (too much)
In the last example, either I can shorten the circuit to 33m OR I'm forced to use 4mm cable (expensive/overkill?)
OR am I allowed to accept that I'll never realistically run 32amps on the ring, therefore the voltage drop *should* be OK?
I guess radials are easier to work out.
16m on 2.5mm cable, 20amp RCBO
18x20x16/1000 = 5.76 volt drop...perfect!
Advice gladly received...
edited tio add - all being done under LBCO oversight/control...