Volt drop is calculated using ohms law
U = I x R
U is the cable volt drop
I is the circuit current (A)
R is the circuit resistance W(ohms)
Volt drop is allowed as 4% of 230V which is 9.2V
For the everyday standard standard multicore pvc insulated cables we can use this table:
http://www.tlc-direct.co.uk/Figures/Tab4.7.htm
for 2.5 mm cable volt drop is 18 mV/A/m (millivolts per ampere per metre of cable.
So multiply that value by the current the cable is actually carrying and then by the length. Divide your answer by 1000 and you get the volt drop value. This value should be less than 9.2v.
I get this upto now.
Is the current the cable is carrying the design current?
Im obviously wrong here, but if I take the current the cable is carrying as 32A, multiply it 18, then a length of say 50m, then divide it by 1000 I get 28.8V drop. This obviously isn’t right so my figure for design current must be wrong?
U = I x R